Date: 17/06/2013 18:56:00
From: Riff-in-Thyme
ID: 331770
Subject: dc adapter adapting

If I wanted to run two 5v appliances off one adapter would I use a 5v apater or a 10-12v?

Reply Quote

Date: 17/06/2013 18:57:31
From: Stealth
ID: 331771
Subject: re: dc adapter adapting

Riff-in-Thyme said:


If I wanted to run two 5v appliances off one adapter would I use a 5v apater or a 10-12v?

A 5v with enough amps for your required draw.

Reply Quote

Date: 17/06/2013 18:57:33
From: Boris
ID: 331772
Subject: re: dc adapter adapting

5v. need to look at current draw though.

Reply Quote

Date: 17/06/2013 18:58:41
From: Riff-in-Thyme
ID: 331773
Subject: re: dc adapter adapting

Boris said:


5v. need to look at current draw though.

okey dokey

Reply Quote

Date: 17/06/2013 18:59:00
From: Stealth
ID: 331774
Subject: re: dc adapter adapting

Riff-in-Thyme said:


If I wanted to run two 5v appliances off one adapter would I use a 5v apater or a 10-12v?

You could only use a 10v supply if both appliances were identical draw, and then you would have to run them in series.

Reply Quote

Date: 17/06/2013 18:59:15
From: Boris
ID: 331775
Subject: re: dc adapter adapting

so 5v and add the two Amps together to get the required current.

Reply Quote

Date: 17/06/2013 19:00:05
From: Riff-in-Thyme
ID: 331776
Subject: re: dc adapter adapting

Stealth said:


Riff-in-Thyme said:

If I wanted to run two 5v appliances off one adapter would I use a 5v apater or a 10-12v?

You could only use a 10v supply if both appliances were identical draw, and then you would have to run them in series.

I guess that is one option but then I’d still have to look at the other

Reply Quote

Date: 17/06/2013 19:01:34
From: Riff-in-Thyme
ID: 331779
Subject: re: dc adapter adapting

Boris said:


so 5v and add the two Amps together to get the required current.

remarkably my maths just covers adding two items together ;)

Reply Quote

Date: 17/06/2013 19:04:43
From: KJW
ID: 331782
Subject: re: dc adapter adapting

Riff-in-Thyme said:


Stealth said:

Riff-in-Thyme said:

If I wanted to run two 5v appliances off one adapter would I use a 5v apater or a 10-12v?

You could only use a 10v supply if both appliances were identical draw, and then you would have to run them in series.

I guess that is one option but then I’d still have to look at the other

It’s not really an option because it also assumes that the load is passive, which is unlikely.

Reply Quote

Date: 17/06/2013 19:06:25
From: Riff-in-Thyme
ID: 331786
Subject: re: dc adapter adapting

KJW said:


Riff-in-Thyme said:

Stealth said:

You could only use a 10v supply if both appliances were identical draw, and then you would have to run them in series.


I guess that is one option but then I’d still have to look at the other

It’s not really an option because it also assumes that the load is passive, which is unlikely.

analogue to digital audio converter(1 each way)

Reply Quote

Date: 17/06/2013 19:08:06
From: Stealth
ID: 331791
Subject: re: dc adapter adapting

Riff-in-Thyme said:


KJW said:

Riff-in-Thyme said:

I guess that is one option but then I’d still have to look at the other

It’s not really an option because it also assumes that the load is passive, which is unlikely.

analogue to digital audio converter(1 each way)


Then you need a 5 v supply, and possibly a regulated 5v supply.

Reply Quote

Date: 17/06/2013 19:09:28
From: Riff-in-Thyme
ID: 331792
Subject: re: dc adapter adapting

Stealth said:


Riff-in-Thyme said:

KJW said:

It’s not really an option because it also assumes that the load is passive, which is unlikely.

analogue to digital audio converter(1 each way)


Then you need a 5 v supply, and possibly a regulated 5v supply.

it’ll be a jaycar raid

Reply Quote

Date: 17/06/2013 19:09:54
From: Stealth
ID: 331793
Subject: re: dc adapter adapting

Stealth said:


Riff-in-Thyme said:

KJW said:

It’s not really an option because it also assumes that the load is passive, which is unlikely.

analogue to digital audio converter(1 each way)


Then you need a 5 v supply, and possibly a regulated 5v supply.


‘Or’ not ‘and’

Reply Quote

Date: 17/06/2013 19:11:11
From: KJW
ID: 331795
Subject: re: dc adapter adapting

Riff-in-Thyme said:


KJW said:

It’s not really an option because it also assumes that the load is passive, which is unlikely.

analogue to digital audio converter(1 each way)

Then no. That load would be active (ie transistors).

Reply Quote

Date: 17/06/2013 19:15:19
From: wookiemeister
ID: 331796
Subject: re: dc adapter adapting

Riff-in-Thyme said:


If I wanted to run two 5v appliances off one adapter would I use a 5v apater or a 10-12v?

a 5V adapter that can provide enough current to power the two devices

eg

each 5V appliance consumes 1A

therefore you need an adaptor that can provide 5V 2A

Reply Quote

Date: 17/06/2013 19:16:36
From: Riff-in-Thyme
ID: 331797
Subject: re: dc adapter adapting

wookiemeister said:


Riff-in-Thyme said:

If I wanted to run two 5v appliances off one adapter would I use a 5v apater or a 10-12v?

a 5V adapter that can provide enough current to power the two devices

eg

each 5V appliance consumes 1A

therefore you need an adaptor that can provide 5V 2A

:)

Reply Quote

Date: 17/06/2013 19:18:25
From: wookiemeister
ID: 331798
Subject: re: dc adapter adapting

you’ll find that most adaptors will have some kind of regulating circuit built into them

the next thing you should be thinking about how you are going to supply two devices from one power source

Reply Quote

Date: 17/06/2013 19:21:25
From: wookiemeister
ID: 331800
Subject: re: dc adapter adapting

voltage is only a measure of electrical pressure

current is a measure of electrons flowing

a 5V device is designed to only have a certain amount of electrical pressure feeding it ie 5V

Reply Quote

Date: 17/06/2013 19:22:52
From: Riff-in-Thyme
ID: 331801
Subject: re: dc adapter adapting

wookiemeister said:


voltage is only a measure of electrical pressure

current is a measure of electrons flowing

a 5V device is designed to only have a certain amount of electrical pressure feeding it ie 5V

I’ve been wookstructed

Reply Quote

Date: 17/06/2013 19:25:56
From: sibeen
ID: 331802
Subject: re: dc adapter adapting

wookiemeister said:

the next thing you should be thinking about how you are going to supply two devices from one power source

Personally, I’d use wires.

Reply Quote

Date: 17/06/2013 19:26:49
From: Stealth
ID: 331803
Subject: re: dc adapter adapting

sibeen said:


wookiemeister said:

the next thing you should be thinking about how you are going to supply two devices from one power source

Personally, I’d use wires.


Old fart. It’s all wireless these days…

Reply Quote

Date: 17/06/2013 19:26:57
From: wookiemeister
ID: 331804
Subject: re: dc adapter adapting

in practical terms

use two 5V adapators

its going to get too messy otherwise

plus if one adaptor flakes out you’ll still have one device that works

Reply Quote

Date: 17/06/2013 19:28:11
From: wookiemeister
ID: 331806
Subject: re: dc adapter adapting

sibeen said:


wookiemeister said:

the next thing you should be thinking about how you are going to supply two devices from one power source

Personally, I’d use wires.


for someone who’s asking this kind of question the best option is to use two power adaptors rather than them splicing and connecting without knowing what they are doing

Reply Quote

Date: 17/06/2013 19:29:12
From: Riff-in-Thyme
ID: 331808
Subject: re: dc adapter adapting

wookiemeister said:


sibeen said:

wookiemeister said:

the next thing you should be thinking about how you are going to supply two devices from one power source

Personally, I’d use wires.


for someone who’s asking this kind of question the best option is to use two power adaptors rather than them splicing and connecting without knowing what they are doing

Mostly need to know what to look for at the shop

Reply Quote

Date: 17/06/2013 19:34:41
From: wookiemeister
ID: 331813
Subject: re: dc adapter adapting

Riff-in-Thyme said:


wookiemeister said:

sibeen said:

Personally, I’d use wires.


for someone who’s asking this kind of question the best option is to use two power adaptors rather than them splicing and connecting without knowing what they are doing

Mostly need to know what to look for at the shop


i’d just buy two adaptors if I were you

what does the connection look like as in what does the jack look like? what kind of plug head would you need?

oh yes if you are using a plug going into a jack have a look at how the device tells you what kind of polarity is needed

some plug heads will have positive in the centre or if you position the head the other way it makes the positive on the outside connection – normally the thing you are powering will have some clue somewhere on it (a small diagram telling you positive centre or outside)

Reply Quote

Date: 17/06/2013 20:13:57
From: KJW
ID: 331873
Subject: re: dc adapter adapting

KJW said:


Riff-in-Thyme said:

KJW said:

It’s not really an option because it also assumes that the load is passive, which is unlikely.

analogue to digital audio converter(1 each way)

Then no. That load would be active (ie transistors).

Actually, there’s a more significant reason why the series option is not an option. Even if one could balance the loads, the grounds would be at different potentials.

Reply Quote

Date: 17/06/2013 20:25:13
From: transition
ID: 331878
Subject: re: dc adapter adapting

>>Actually, there’s a more significant reason why the series option is not an option. Even if one could balance the loads, the grounds would be at different potentials”

Reminds me of all those UHF radio warranty returns when they first came out, farmers would pick the wrong battery of their two twelve volt batteries in series and the antenna base or radio chassis would ground, and, well, 12+12=24.

Reply Quote

Date: 17/06/2013 20:27:47
From: wookiemeister
ID: 331879
Subject: re: dc adapter adapting

changing subject

have you have a leg twitch that happens once in a blue moon?

I just had one, I started feeling it somewhere along my spine , travelling down my leg to the foot then bang, the whole leg twitches

Reply Quote

Date: 17/06/2013 20:42:12
From: transition
ID: 331881
Subject: re: dc adapter adapting

>>I just had one, I started feeling it somewhere along my spine , travelling down my leg to the foot then bang, the whole leg twitches.

Bit of a thread derailment, but broadly electrical I suppose.
Not today, no, don’t believe i’ve even had an involuntary erection for a couple of days.
I’m sure you were wondering about exactly that but were too shy to ask.

Reply Quote

Date: 17/06/2013 20:46:08
From: Riff-in-Thyme
ID: 331882
Subject: re: dc adapter adapting

“http://www.sciencedaily.com/releases/2013/06/130614140504.htm”

Mystery of X-Ray Light from Black Holes Solved
June 14, 2013 — It is a mystery that has stymied astrophysicists for decades: how do black holes produce so many high-power X-rays?

In a new study, astrophysicists from The Johns Hopkins University, NASA and the Rochester Institute of Technology conducted research that bridges the gap between theory and observation by demonstrating that gas spiraling toward a black hole inevitably results in X-ray emissions.

Reply Quote

Date: 17/06/2013 21:02:30
From: sibeen
ID: 331884
Subject: re: dc adapter adapting

KJW said:


KJW said:

Riff-in-Thyme said:

analogue to digital audio converter(1 each way)

Then no. That load would be active (ie transistors).

Actually, there’s a more significant reason why the series option is not an option. Even if one could balance the loads, the grounds would be at different potentials.

Nyet, no earth reference.

Reply Quote

Date: 17/06/2013 21:10:41
From: wookiemeister
ID: 331885
Subject: re: dc adapter adapting

transition said:


>>I just had one, I started feeling it somewhere along my spine , travelling down my leg to the foot then bang, the whole leg twitches.

Bit of a thread derailment, but broadly electrical I suppose.
Not today, no, don’t believe i’ve even had an involuntary erection for a couple of days.
I’m sure you were wondering about exactly that but were too shy to ask.


you know me too well

how long has it been happening fsm?

the first step is to stop the denial

Reply Quote

Date: 17/06/2013 21:29:45
From: KJW
ID: 331892
Subject: re: dc adapter adapting

sibeen said:


KJW said:

Actually, there’s a more significant reason why the series option is not an option. Even if one could balance the loads, the grounds would be at different potentials.

Nyet, no earth reference.

I think you would find that the potential difference between the grounds of the two devices powered in series from the one 10V power adapter would be 5V or thereabouts.

Reply Quote

Date: 17/06/2013 21:36:48
From: KJW
ID: 331896
Subject: re: dc adapter adapting

KJW said:


sibeen said:

Nyet, no earth reference.

I think you would find that the potential difference between the grounds of the two devices powered in series from the one 10V power adapter would be 5V or thereabouts.

The potential of the two devices may be floating but one device will still be 5V or thereabouts above the other device.

Reply Quote

Date: 17/06/2013 21:46:32
From: morrie
ID: 331904
Subject: re: dc adapter adapting

KJW said:


KJW said:

sibeen said:

Nyet, no earth reference.

I think you would find that the potential difference between the grounds of the two devices powered in series from the one 10V power adapter would be 5V or thereabouts.

The potential of the two devices may be floating but one device will still be 5V or thereabouts above the other device.


Of course, but does that matter?

Reply Quote

Date: 17/06/2013 21:49:52
From: KJW
ID: 331908
Subject: re: dc adapter adapting

morrie said:


KJW said:

KJW said:

I think you would find that the potential difference between the grounds of the two devices powered in series from the one 10V power adapter would be 5V or thereabouts.

The potential of the two devices may be floating but one device will still be 5V or thereabouts above the other device.


Of course, but does that matter?

If you want to connect them either to each other or to something else common to both, then yes it does matter.

Reply Quote

Date: 17/06/2013 21:56:45
From: sibeen
ID: 331911
Subject: re: dc adapter adapting

KJW said:


morrie said:

KJW said:

The potential of the two devices may be floating but one device will still be 5V or thereabouts above the other device.


Of course, but does that matter?

If you want to connect them either to each other or to something else common to both, then yes it does matter.

Yes, if you wish to bus the devices together it will be an issue, if not then it won’t be an issue.

Of course, I still wouldn’t do it :)

Reply Quote

Date: 17/06/2013 21:57:52
From: morrie
ID: 331912
Subject: re: dc adapter adapting

KJW said:


morrie said:

KJW said:

The potential of the two devices may be floating but one device will still be 5V or thereabouts above the other device.


Of course, but does that matter?

If you want to connect them either to each other or to something else common to both, then yes it does matter.


If they are in series, then they are connected to each other by definition, aren’t they?
I see what you mean about connecting them both to something else though. That might be a problem.

Reply Quote

Date: 17/06/2013 22:00:24
From: transition
ID: 331916
Subject: re: dc adapter adapting

>>Of course, but does that matter?

Generally you keep rails uniform to avoid complications and accidents. Common grounds make it all a bit easier to think about too.

Beyond the problem of unbalanced loads creating inproper voltages in the case the supply weren’t regulated, you could ground the centre which’d have it be like a +/- split supply, if you wanted.

Reply Quote

Date: 17/06/2013 22:05:26
From: gaghalfrunt
ID: 331926
Subject: re: dc adapter adapting

I love these topics where advice abounds despite almost universal ignorance of the subject.

Reply Quote

Date: 17/06/2013 22:06:54
From: roughbarked
ID: 331929
Subject: re: dc adapter adapting

gaghalfrunt said:


I love these topics where advice abounds despite almost universal ignorance of the subject.

That’s why I’m only watching.

Reply Quote

Date: 17/06/2013 22:12:22
From: wookiemeister
ID: 331936
Subject: re: dc adapter adapting

gaghalfrunt said:


I love these topics where advice abounds despite almost universal ignorance of the subject.

it starts after the question has been answered

there wouldn’t be a voltage difference between “grounds” or earth or a return circuit

1 there would most likely be no earth involved

2 the return circuits are connected so no voltage difference would be found in a parallel circuit

Reply Quote

Date: 17/06/2013 22:30:25
From: transition
ID: 331942
Subject: re: dc adapter adapting

>>I love these topics where advice abounds despite almost universal ignorance of the subject.

My mum was a diode.

Reply Quote

Date: 17/06/2013 22:34:25
From: KJW
ID: 331944
Subject: re: dc adapter adapting

wookiemeister said:


there wouldn’t be a voltage difference between “grounds” or earth or a return circuit

1 there would most likely be no earth involved

2 the return circuits are connected so no voltage difference would be found in a parallel circuit

I have considered the idea of powering two devices from the one power adapter (connected in parallel), and consider it to be a bad idea. With two power adapters separately powering the two devices, the two devices have independently floating voltages, and the ground wire that connects the two devices is what determines the internal voltages of one device relative to the internal voltages of the other device. But when the one power adapter powers both devices, then the internal voltages of one device relative to the internal voltages of the other device are already determined without connecting the devices together via the ground wire. Thus, when the devices are connected together via the ground wire, there is strong risk of creating a ground loop.

Reply Quote

Date: 17/06/2013 22:48:06
From: sibeen
ID: 331951
Subject: re: dc adapter adapting

KJW said:


wookiemeister said:

there wouldn’t be a voltage difference between “grounds” or earth or a return circuit

1 there would most likely be no earth involved

2 the return circuits are connected so no voltage difference would be found in a parallel circuit

I have considered the idea of powering two devices from the one power adapter (connected in parallel), and consider it to be a bad idea. With two power adapters separately powering the two devices, the two devices have independently floating voltages, and the ground wire that connects the two devices is what determines the internal voltages of one device relative to the internal voltages of the other device. But when the one power adapter powers both devices, then the internal voltages of one device relative to the internal voltages of the other device are already determined without connecting the devices together via the ground wire. Thus, when the devices are connected together via the ground wire, there is strong risk of creating a ground loop.

KJW, that makes no sense to me. The output of a power adaptor is floating, as you have mentioned. How is a ‘ground loop’ going to be established?

If it was an isolated 5V battery would you have the same concerns?

Reply Quote

Date: 17/06/2013 22:56:38
From: wookiemeister
ID: 331960
Subject: re: dc adapter adapting

KJW said:


wookiemeister said:

there wouldn’t be a voltage difference between “grounds” or earth or a return circuit

1 there would most likely be no earth involved

2 the return circuits are connected so no voltage difference would be found in a parallel circuit

I have considered the idea of powering two devices from the one power adapter (connected in parallel), and consider it to be a bad idea. With two power adapters separately powering the two devices, the two devices have independently floating voltages, and the ground wire that connects the two devices is what determines the internal voltages of one device relative to the internal voltages of the other device. But when the one power adapter powers both devices, then the internal voltages of one device relative to the internal voltages of the other device are already determined without connecting the devices together via the ground wire. Thus, when the devices are connected together via the ground wire, there is strong risk of creating a ground loop.


it all depends on the load

i’m assuming that this device could just use two separate powersupplies

in this case with the load the first place to start about how the load should be powered is with the manual

how does the manual say the load should be powered?

Reply Quote

Date: 17/06/2013 23:06:39
From: KJW
ID: 331962
Subject: re: dc adapter adapting

sibeen said:


KJW said:

I have considered the idea of powering two devices from the one power adapter (connected in parallel), and consider it to be a bad idea. With two power adapters separately powering the two devices, the two devices have independently floating voltages, and the ground wire that connects the two devices is what determines the internal voltages of one device relative to the internal voltages of the other device. But when the one power adapter powers both devices, then the internal voltages of one device relative to the internal voltages of the other device are already determined without connecting the devices together via the ground wire. Thus, when the devices are connected together via the ground wire, there is strong risk of creating a ground loop.

KJW, that makes no sense to me. The output of a power adaptor is floating, as you have mentioned. How is a ‘ground loop’ going to be established?

If it was an isolated 5V battery would you have the same concerns?

Maybe I’m using the term “ground loop” inappropriately, but the point is that each device will create its own ground reference relative to the power supply rails, and the two devices may do this differently so that the ground reference of one device relative to the negative rail will differ from the ground reference relative to the negative rail in the other device. For two separate power supplies, this is not a problem. But for one common power supply, the two grounds will then be at different voltages and when connected together, a current will flow.

Reply Quote

Date: 17/06/2013 23:14:16
From: wookiemeister
ID: 331964
Subject: re: dc adapter adapting

KJW said:


sibeen said:

KJW said:

I have considered the idea of powering two devices from the one power adapter (connected in parallel), and consider it to be a bad idea. With two power adapters separately powering the two devices, the two devices have independently floating voltages, and the ground wire that connects the two devices is what determines the internal voltages of one device relative to the internal voltages of the other device. But when the one power adapter powers both devices, then the internal voltages of one device relative to the internal voltages of the other device are already determined without connecting the devices together via the ground wire. Thus, when the devices are connected together via the ground wire, there is strong risk of creating a ground loop.

KJW, that makes no sense to me. The output of a power adaptor is floating, as you have mentioned. How is a ‘ground loop’ going to be established?

If it was an isolated 5V battery would you have the same concerns?

Maybe I’m using the term “ground loop” inappropriately, but the point is that each device will create its own ground reference relative to the power supply rails, and the two devices may do this differently so that the ground reference of one device relative to the negative rail will differ from the ground reference relative to the negative rail in the other device. For two separate power supplies, this is not a problem. But for one common power supply, the two grounds will then be at different voltages and when connected together, a current will flow.


the manual for the load should show it should be powered

Reply Quote

Date: 17/06/2013 23:19:33
From: sibeen
ID: 331969
Subject: re: dc adapter adapting

KJW said:


sibeen said:

KJW said:

I have considered the idea of powering two devices from the one power adapter (connected in parallel), and consider it to be a bad idea. With two power adapters separately powering the two devices, the two devices have independently floating voltages, and the ground wire that connects the two devices is what determines the internal voltages of one device relative to the internal voltages of the other device. But when the one power adapter powers both devices, then the internal voltages of one device relative to the internal voltages of the other device are already determined without connecting the devices together via the ground wire. Thus, when the devices are connected together via the ground wire, there is strong risk of creating a ground loop.

KJW, that makes no sense to me. The output of a power adaptor is floating, as you have mentioned. How is a ‘ground loop’ going to be established?

If it was an isolated 5V battery would you have the same concerns?

Maybe I’m using the term “ground loop” inappropriately, but the point is that each device will create its own ground reference relative to the power supply rails, and the two devices may do this differently so that the ground reference of one device relative to the negative rail will differ from the ground reference relative to the negative rail in the other device. For two separate power supplies, this is not a problem. But for one common power supply, the two grounds will then be at different voltages and when connected together, a current will flow.

I must admit that you’re losing me here.

If a device is powered from a 5 volt supply, normally the negative of the supply will be considered to be the ground – whether there is an actual connection to a ground reference or not. Now if both devices are connected to the same supply then the positive rail and the negative rails are going to be at the same potential. How do the grounds differ in this case?

> but the point is that each device will create its own ground reference relative to the power supply rails

The negative rail will be the groung reference.

Reply Quote

Date: 17/06/2013 23:24:18
From: KJW
ID: 331974
Subject: re: dc adapter adapting

KJW said:


Maybe I’m using the term “ground loop” inappropriately, but the point is that each device will create its own ground reference relative to the power supply rails, and the two devices may do this differently so that the ground reference of one device relative to the negative rail will differ from the ground reference relative to the negative rail in the other device. For two separate power supplies, this is not a problem. But for one common power supply, the two grounds will then be at different voltages and when connected together, a current will flow.

If you could be sure that both devices are using the negative rail as the ground reference, then this it will be fine. But it requires that one knows the internal circuitry of the two devices to be sure. However, for audio devices, the ground is usually midway between the rails. Even if both audio devices have their grounds set midway between the rails, the two ground voltages might not be precisely equal because this depends on the tolerances of the components that split the power supply. Thus, one may still have a small current between the grounds of the two devices, and for high-fidelity audio, this is a bad thing.

Reply Quote

Date: 17/06/2013 23:28:52
From: transition
ID: 331981
Subject: re: dc adapter adapting

To indulge

If you used a single 10 Volt plug pack say, and were crazy enough to split it rather than just dropping the voltage down, you could use the two series loads as a rough voltage divider, but really you have to regulate that centre voltage relative to +/- rails . This way if the outputs are some AC or digital signal and meet each other somewhere you might drop a capacitor in the line and isolate/couple them, and you have the common ground so outputs don’t influence each other in undesirable ways or the entire arrangements. Of course a capacitor isn’t required, you could throw in a transistor or fet or whatever and have both looking like operating between the same supply rails. If the phase relationship between the two were important it’d be a bit more demanding maybe.

Shuteye time.

Reply Quote

Date: 17/06/2013 23:29:23
From: sibeen
ID: 331985
Subject: re: dc adapter adapting

It’s an A/D converter. I’d be very surprised if a split rail system was used, actually, I’d be stunned:)

Reply Quote

Date: 17/06/2013 23:30:00
From: KJW
ID: 331987
Subject: re: dc adapter adapting

sibeen said:


I must admit that you’re losing me here.

If a device is powered from a 5 volt supply, normally the negative of the supply will be considered to be the ground – whether there is an actual connection to a ground reference or not. Now if both devices are connected to the same supply then the positive rail and the negative rails are going to be at the same potential. How do the grounds differ in this case?

> but the point is that each device will create its own ground reference relative to the power supply rails

The negative rail will be the groung reference.

It should be kept in mind that I’m talking about a situation where one device outputs a signal voltage to the other device’s input. The ground wire that connects the two devices is the ground reference I’m referring to and this need not be the same as the power supply rails.

Reply Quote

Date: 17/06/2013 23:34:30
From: transition
ID: 331996
Subject: re: dc adapter adapting

>>It’s an A/D converter. I’d be very surprised if a split rail system was used, actually, I’d be stunned:)”

The point though is the crazy indulgence of getting two 5 Volt supplies for two 5 Volt devices from a single 10 Volt supply without simply dropping the voltage down to 5 Volts, along with the possibility they may meet somewhere.

Reply Quote

Date: 17/06/2013 23:36:46
From: KJW
ID: 332002
Subject: re: dc adapter adapting

sibeen said:


It’s an A/D converter. I’d be very surprised if a split rail system was used, actually, I’d be stunned:)

I was speaking in more general terms, but even for an A/D converter, there is still the analogue side to consider.

Reply Quote

Date: 20/06/2013 00:44:10
From: Martins
ID: 333228
Subject: re: dc adapter adapting

you probably have a few 5v adapters at home already.

nearly every phone, camera, etc uses 5v supply. USB chargers etc will be 5v

Reply Quote

Date: 21/06/2013 01:05:53
From: KJW
ID: 333809
Subject: re: dc adapter adapting

Martins said:


you probably have a few 5v adapters at home already.

nearly every phone, camera, etc uses 5v supply. USB chargers etc will be 5v

The reason I wanted to use a single power supply to power multiple devices was to get rid of all those adapters which take up so much space on a power-board.

Reply Quote

Date: 21/06/2013 07:59:54
From: Riff-in-Thyme
ID: 333824
Subject: re: dc adapter adapting

KJW said:


Martins said:

you probably have a few 5v adapters at home already.

nearly every phone, camera, etc uses 5v supply. USB chargers etc will be 5v

The reason I wanted to use a single power supply to power multiple devices was to get rid of all those adapters which take up so much space on a power-board.

exactly. i have 9 going as it is

Reply Quote

Date: 27/06/2013 09:09:11
From: Martins
ID: 337526
Subject: re: dc adapter adapting

Riff-in-Thyme said:


KJW said:

Martins said:

you probably have a few 5v adapters at home already.

nearly every phone, camera, etc uses 5v supply. USB chargers etc will be 5v

The reason I wanted to use a single power supply to power multiple devices was to get rid of all those adapters which take up so much space on a power-board.

exactly. i have 9 going as it is

Roger,

Find one with a good capacity. The newer apple chargers are 10w (so two amp), and use it to power two devices that require 10w or less in total.

In fact connect as many as you like, as long as total power requirement is less than power capacity of the plug pack.

Connect devices in parallel.

The point being this is a better idea than a 10v charger with the devices in series.

Reply Quote