powerpoint checkers are nice but you should be aware of their limitations , in my opinion…..
if the earth has some unexpected resistance on it the checker won’t see this because it draws very little current – all it sees is the earth drawing enough to power an LED
a transposed neutral earth won’t be picked up because the customer neutral and earth bar are at the same voltage (0V)
fairly much true i’d reckon.
now, which transposed liven up the body of earthed things, or give you a short, or leakage(RCD), that’ll throw the breaker, that sort of thing. What’s dangerous?
with RCD any difference between A and N over the 30mA typical trip threshold or whatever will do it. So I guess this means N and E reversed will trip it (when >30mA load applied).
A and E reversed will trip it (that’d typically liven a chassis earth) in the case there is some path to ground resulting in >30mA, like a human touching the metal body of something (that’d ordinarily be earthed), plumbing, or a power tool laying on damp ground.
A and N reversed typically doesn’t make much difference (of single phase), other than the circuits become a dog’s breakfast to think about. Like switches that are usually in the active line are in the neutral, and appliances are powered up via the neutral right through them (the load) back to the switch.
the nastiest possibility I guess is reversing A and E when there’s no RCD, just a standard circuit breaker. The next nastiest is an absence of an earth when it’s needed in the case of leakage or short to what usually would be earthed parts of equipment.
i’m sure there’s other possibilities, like getting all three wires wrong, but think that’s covered in those above.
of course if you lose the neutral on your service line (out on the pole/in the street, which is also an earth), and the dogs chewed your earth wire off the earth stake outside your house, then nothing in your house is safe.
need an aspirin after that